Battle-Tested Diesel Generators and Parts › Forums › Military Generator Troubleshooting › Mep 803A no power › Reply To: Mep 803A no power
August 2, 2025 at 11:05 am
#20699
Participant
I have been following TM 9-6115-642-24 there is a test procedure for the ac circuit interrupter and circuits before this S5 switch. Every test has been followed and check out acceptable. I have 120/240 to the feed side and nothing to the load side. I am sure it is the 24 low volt feed to this interrupter. I am not getting 24volts when I hold up the ac circuit switch on the instrument panel. Anyone have any thoughts as to why I am not getting 24v dc to the s5?
Thank You
Bob