Reply To: MEP003A only produces 130 volts
Battle-Tested Diesel Generators and Parts › Forums › Military Generator Troubleshooting › MEP003A only produces 130 volts › Reply To: MEP003A only produces 130 volts
October 8, 2024 at 2:33 pm
#20133
Participant
Hmmm… 130v is suspicious…. Is it really 130v? Check real voltage at AC outlet on front panel…
Should be a clean 120v on each L1, L2, L3 settting…
Are ALL selector settings the same voltage? That should never happen!
Only the L1-L2, L2-L3, L1-L3 settings should be 240v….
Check your earth ground? It Should be connected to a rod 6’-8’ in the ground, or tied to rebar in a concrete slab… and N&G should be connected together at the terminal block…