MEP805-A troubleshooting Low VAC Output

Battle-Tested Diesel Generators and Parts Forums Military Generator Troubleshooting MEP805-A troubleshooting Low VAC Output

Viewing 0 reply threads
  • Author
    Posts
    • #5723
      troutbum_007
      Participant

      I have been tasked with troubleshooting a pair of MEP805-A Generators,which are both running fine (and at correct frequencies), but will only make very low AC Voltage…The average L-L VAC between the two is about 18, and the average L-N VAC is about 30…and these readings are consistent across all 3 phases, which in my experience, generally rules out faulty diodes in Rotating Rectifiers, Exciter Stators or AVR’s…So Per the DS (24) Manual, this condition otherwise only indicates either faulty Power Potential Transformers, or faulty Generator Stator Housing Assemblies…Both units have been in a fairly damp humid environment near ocean for an extended time, without exercise…Anyone else ever experience these odd issues, and where could I even buy the parts required to fix?