      GMG
      Keymaster

      This topic is dedicated to all troubleshooting, technical questions, and other questions related to the MEP802A and MEP803A military diesel generators.

    • #2288
      mkocci
      Participant

      Hi there, I just acquired an MEP-803A from Camp Pendleton.
      All the fluids and the batteries had been removed.
      I have installed 2 new batteries, added coolant and oil. I have not yet added fuel.
      My problem is that when I hit the start switch, nothing happens.
      I have 25 volts at the batteries, and 25 volts at the MT-4 fusible link behind the panel.
      It will crank like a champ when I hit the dead start switch.
      Am I missing something? Is their a low fuel cut off switch?
      I get no power to any of the lights or gauges on the panel.
      Thank you
      Kevin

    • #3459
      Loren
      Participant

      Ordered fuel pump received a newer model fuel pump that appears not to install the same. needs additional filter and fittings. Anyway to get original replacement part? 802A 1993 model 5kw diesel or jet fuel

    • #5725
      jkpdigital
      Participant

      I’m having trouble finding a circuit breaker fuse my MEP-802a. I’ve looked everywhere with no success in finding one. The number on the old fuse is: FO3 125V 30A. Is is also a ceramic fuse. Anybody have suggestions as to where to find these fuses, or what would be the replacement for it? Thanks for any help.

    • #6742
      rboling
      Participant

      Having trouble with high coolant temp light and shutting down, coolant level is good, temp light comes on quickly and shuts off, not even showing temp change on gauge, other times comes on after a minute or two, sometimes temp gauge goes high as well? help

    • #8197
      talltexanjack
      Participant

      Does anyone know the output psi of the injection pump? Thanks

    • #9014
      Bruce
      Participant

      My MEP802A will not shut down. Battle short is off. Nothing will make it stop. Even tried blocking air intake! What can I do?

    • #13414
      joseph.mesa
      Participant

      Hi,
      I just bought a generator set military type MEP 803A and having problems with the voltage and frequency meter. Anyone encountering this and/or have encountered this and was able to fix it.
      Pls send info to joseph.mesa@gmail.com

    • #13460
      283patrick
      Member

      802a ran for a week or two aok, then died, had to replace start switch, replaced alternator. Unit now runs, but generator only puts out 24vac. Suspect glazed brushes. Anybody know how to put an external voltage on the generator output to break the glaze? Also, anybody ever replaced the generator brushes. The unit is trailered on a pu 797?

    • #14694
      Ruffrider
      Participant

      Having same problem will turn over like crazy using work crank but only get a click on master switch???

    • #14833
      wa0dfw
      Participant

      I’m not sure if I’m doing this right. I just found this page and am not highly computer savvy.
      I just obtained an MEP-003A 10KW generator with a Lister-Petter engine. I’m having problems finding info on this unit. Like others, all the fluids were drained. So far I haven’t been able to figure out why I don’t seem to be getting fuel to the injectors but haven’t been able to find any info on that particular (water cooled) engine.
      Help is needed on the proper manual and that engine. I don’t seem to find am engine on Green Mountain’s list of Lister-Petter engines that looks like a likely suspect either.
      I’m pleading and begging for help!
      Thanks, Leonard

    • #17285
      Jamie Near
      Participant

      Hello, I have a question on the way the remote start kits work for my MEP802 generator. The kit works fine but it seems that if the generator doesn’t auto start the first crank cycle due to cold weather the controller doesn’t try starting a second or third time. How does the remote start controller PCB work? Should it try 3 times to start and then lock out? I don’t see this sequence of operation covered in the manual.

    • #18472
      Mark Damele
      Participant

      Governor stuck in the off position when the engine is cranking and the shutdown solenoid is on.
      Does anyone know how to get it working?

    • #18478
      keystone
      Participant

      I have a 275 gallon fuel tank conected to my mep802a.When master switch is in the Aux fuel position fuel floods out of the on board fuel tank.If left in the Aux position the entire 275 gallons will be on the floor in a matter of a few hours. Please help

    • #18479
      meshew75
      Participant

      @keystone

      Sounds like your float is stuck

    • #18482
      keystone
      Participant

      Does the onboard fuel float control the aux fuel pump?

    • #18483
      meshew75
      Participant

      The float does two things, low fuel shut off and aux pump on/off
      There has been talk of fuel pushing through the aux pump when using a large bulk tank
      I added a fuel solinoid inline with the aux pump on mine just to be sure
      I believe the float can be activated through the fuel filler by pulling the screen out
      Unplug your main fuel pump when testing, maked it easier to hear the aux pump
      Also check out Steel Solders, there are many discussions about the MEP 8xx series generators

    • #18634
      Darius Gray
      Participant

      Friend has a 802. Runs his whole house just fine, except for an old 7hp air compresssor. Switching it on the gen bogs down to nearly stall and puts out black smoke. THe compressor is on a 20a breaker on the panel. Ideas on what to check for? Can it really be too much for the gen at <20a?

      • #18637
        Mark Damele
        Participant

        This not going to work
        3 phase 7 hp motor should draw 16 – 20 amps @ 240volts
        the generator is rated at 17 amps @ 3 ph 208 volts
        The inrush will be much greater.
        1 phase 7 hp motor should draw 29 amps @ 230volts
        the generator is rated at 26 amps @ 1 ph 230 volts

    • #18635
      skylinesystemsllc
      Participant

      Inrush current on the compressor could easily exceed 20a, albeit briefly.

    • #19053
      bonuglipaint
      Participant

      802A fuel light comes on and it dies. new fuel, filter. any ideas? starts and run great for a few minutes.
      Thanks

    • #19328
      paul.peria.civ
      Participant

      Anyone by the fuel level from this site with success? Part 88-21103. Says it has 27 in stock on GMG

      • #19329
        paul.peria.civ
        Participant

        Adding on, looking at KUS website, it doesn’t look like these are actually a swap in replacement for the originals.

    • #19766
      tjohnson110505
      Participant

      Fermont MEP-803A 10kW
      Purchased for home usage, drained all old fuel topped off with new. When in aux prime, the aux pump works for aux but when moved into start position for the main tank pump does not have voltage to power pump. First I thought it was the pump, but once I unplugged and put meter on it, it was verified no voltage but the strange part it does when in aux?. could it be the sender in the tank closing the circuit? or am i going about this incorrect??

    • #19767
      Mark Damele
      Participant

      Hello,
      The AUX fuel pump is for adding fuel to the fuel tank. The PRIME fuel pump charges the engine fuel system. First check the CRANK switch, near the fuel filters, on the left side near the door hinge, make sure it’s in the NORMAL or RUN position. If this does not solve the problem then you need to check the fuel level switch or the primary fuel pump and that circuit.

      Mark

    • #19769
      tjohnson110505
      Participant

      Yes, its in normal position. even when in dead crank only aux pump comes on momentary. Thank you I will let you know what the end result is. Also you wouldn’t happen to know what style and or p/n the fuel drain valve and cap is would you, this one is leaking and I really don’t want to drain the fuel just added to match make it.

    • #19778
      Mark Damele
      Participant

      As with any military surplus, the plumbing parts are type “AN”. These are available at any automotive performance shop(Summit, Jrgs, etc.). I did not have a chance to check mine today, but if you read up on them, you should be able to figure it out.
      Mark

    • #19796
      tjohnson110505
      Participant

      Thanks Mark, for anyone else fighting the same thing I found the bottom float was stuck causing the primary pump to trip.

    • #19972
      bonuglipaint
      Participant

      Motor is vibrating and muffler has moved around 1/2 in. under top cover. making noise, I think coming from muffler. Removed top cover for venting. still working, but strong vibration on oil fill side. Thanks for any help.