MEP 802A tripping AC interrupter switch
- This topic has 1 reply, 2 voices, and was last updated 1 year, 1 month ago by .
Viewing 1 reply thread
Viewing 1 reply thread
- You must be logged in to reply to this topic.
Battle-Tested Diesel Generators and Parts › Forums › Military Generator Troubleshooting › MEP 802A tripping AC interrupter switch
Tagged: MEP 802A
generator runs good , powers up house lights, but when a/c unit compressor turns on, a/c circuit interruptor trips. A/C unit is two ton.
That is around a 50amp starting load at 240v. What else is running when you attempt to start AC. Note that this is near the max for an 802A. Nothing is wrong, the load is too big.