The 002A is rated at 5000 watts at its peak it can hit 8500 watts but that only equates to 35 amps. S0 if you are already at 25 percent you do not have the amps there to start a 40 amp HVAC. I have run into this before with even a 10K unit that would not start an air compressor that was rated at 40 amps.