  • in reply to: MEP 802A tripping AC interrupter switch #19044
    GMG
    Keymaster

    That is around a 50amp starting load at 240v. What else is running when you attempt to start AC. Note that this is near the max for an 802A. Nothing is wrong, the load is too big.

    in reply to: MEP-806B Remote Start #18952
    GMG
    Keymaster

    Inova makes a remote start/auto start kit that can work with most ATS systems. Please consult their website.

    in reply to: MEP 002A Within Load Limits Breaker Trip #18832
    GMG
    Keymaster

    Starting amps too high. Nothing wrong with unit. The actual starting amps to start your AC is quite high.

    in reply to: MEP 805 A Generator 30 KW #18790
    GMG
    Keymaster

    Use a 3rd party, external phase converter. Keep the unit stock.

    in reply to: Mep002 Main breaker trips under light load. #18591
    GMG
    Keymaster

    There is a space at the top of the main lugs in the back (about an inch wide). This is the #1 entry point for mice! This must be closed to ensure mice do not take up residence in the distribution box. This is the #1 MOST COMMON source of electrical problems in that box.

    in reply to: Mep002 Main breaker trips under light load. #18590
    GMG
    Keymaster

    Not that we are aware of.

    in reply to: MEP-803A? #18582
    GMG
    Keymaster

    Very broad question. This is a constant speed application and is very different from any kind of vehicle diesel application. These are great units. Diesel fuel and variants are acceptable. But stick to diesel. Do not use Kerosene ever.

    in reply to: Shut down with load #18558
    GMG
    Keymaster

    Could be many things… Make sure your entire fuel system is clean (filters, lines, fuel tank). It needs more fuel under load, so if it calls for it and can’t get it, it will bog down.

    Poor compression or air restriction are possibilities too.

    Obviously, I have no idea what your load is on the unit. I am assuming it’s reasonable and within spec.

    in reply to: Dayton 4w117H 20kw 3 phase generator #18508
    GMG
    Keymaster

    Sorry, do not know about this. I have not heard of a fiat engine in any military units.

    in reply to: MB 17 generator voltage too high #18210
    GMG
    Keymaster

    Seems more like voltage regulator, not a simple adjustment/rheostat issue.

    in reply to: Parts for MEP-805A #18180
    GMG
    Keymaster

    Can you confirm the part numbers you need? You can use our free manuals here. Also, please tell me if you would consider used parts at a discount.

    MEP805A-Technical-Parts-Manual-TM-9-6115-644-24P

    There are A and B variants of this generator and simply want to be sure we are getting you the correct parts.

    in reply to: MEP016B MEP701 not d/c charging the battery #18167
    GMG
    Keymaster

    Are you saying your batteries are NOT being charged, but the battery volt meter is reading “green?” Did you confirm that meter is working properly with an independent tool? The unit always uses the battery for power, but they should be charging when the generator is in use. Perhaps you need a new meter and/or voltage regulator. But if the battery voltage meter is working, then check connection to the batteries from the voltage regulator.

    in reply to: MEP -831 A turns off with camper AC load #18159
    GMG
    Keymaster

    How large is the AC? It seems you don’t believe you are overloading it, but you might be.

    in reply to: A5 Module #18143
    GMG
    Keymaster

    Please consult manuals. Unfortunately, we do not have technical personnel to answer you question.

    in reply to: A5 Module #18141
    GMG
    Keymaster

    Please consult manuals. Unfortunately, we do not have technical personnel to answer you question.

    in reply to: MEP-802A Kerosene as fuel #18121
    GMG
    Keymaster

    I would not.

    in reply to: MEP-806B zero readings #18049
    GMG
    Keymaster

    Sorry, but this is too general of a comment. Need to check master breaker, make sure that the read-out setting corresponds to the desired voltage/phase output you have set. Please download free manuals from out website.

    in reply to: Groban GDC 40-63 #17962
    GMG
    Keymaster
    in reply to: Groban GDC 40-63 #17961
    GMG
    Keymaster
    in reply to: Groban GDC 40-63 #17960
    GMG
    Keymaster

    Sorry, no. I saw some on GovPlanet for sale. That might give you a better NSN number with which to search for manuals.

    in reply to: MEP-803A crank no start #17912
    GMG
    Keymaster

    Before attempting to start any of the auction-purchased units, the entire fuel system must be cleaned thoroughly. All lines blown out, all filters changed. Could be many things going wrong. Check to make sure fuel is getting to each injector. Starter probably hot from over-cranking.

    in reply to: MEP-803A crank no start #17911
    GMG
    Keymaster

    Before attempting to start any of the auction-purchased units, the entire fuel system must be cleaned thoroughly. All lines blown out, all filters changed. Could be many things going wrong. Check to make sure fuel is getting to each injector. Starter probably hot from over-cranking.

    GMG
    Keymaster

    No, these are diesel generators. We do not have recommendations on non-diesel units.

    in reply to: MEP-804-B #17658
    GMG
    Keymaster

    Please look up part number in our Free manuals. We need to be sure of what we are hunting for. We receive dozens of inquiries per day and do not have the time to look up exact part numbers. Some A and B series can use slightly different parts/versions and only a good part number will ensure we are quoting you the correct part. Thanks! GMG

    in reply to: MEP-804-B #17657
    GMG
    Keymaster

    Please look up part number in our Free manuals. We need to be sure of what we are hunting for. We receive dozens of inquiries per day and do not have the time to look up exact part numbers. Some A and B series can use slightly different parts/versions and only a good part number will ensure we are quoting you the correct part. Thanks! GMG

    in reply to: FUEL LINE SIZE’S THAT FEED THE FUEL INJECTORS #17288
    GMG
    Keymaster

    What generator model?

    in reply to: MEP-831 Fuel Sending Unit #17170
    GMG
    Keymaster

    0-30 Ohms

    in reply to: MEP009B no Hertz reading #16944
    GMG
    Keymaster

    Please download free manuals from our website.

    in reply to: MEP009B no Hertz reading #16943
    GMG
    Keymaster

    Have you adjusted the throttle?

    in reply to: MEP009B no Hertz reading #16942
    GMG
    Keymaster

    You should use a known good multimeter and not depend on the on-board meters (just to rule out a bad meter).